Sensor value is ouside the valid range...

Supporting 2.7 and 3.2+
User avatar
mparadis
Site Admin
Posts: 660
Joined: Fri Oct 28, 2011 12:17 pm
Contact:

Re: Sensor value is ouside the valid range...

Post by mparadis »

Based on those numbers I suspect you're using SENSOR_TYPE_1125_HUMIDITY instead of SENSOR_TYPE_1125_TEMPERATURE.
berkinet
Phidgeteer!
Posts: 95
Joined: Thu Sep 17, 2009 12:17 pm
Contact:

Re: Sensor value is ouside the valid range...

Post by berkinet »

Nope. It is set as a temperature device. I am measuring the exit pipe on a hot water system.
User avatar
mparadis
Site Admin
Posts: 660
Joined: Fri Oct 28, 2011 12:17 pm
Contact:

Re: Sensor value is ouside the valid range...

Post by mparadis »

The numbers you gave match up almost perfectly:

0.535 v/v -> 57.766 °C on the 1125's temperature sensor (or 1124)
0.535 v/v -> 61.771 %RH on the 1125's humidity sensor

I tested this on the current version of the control panel and I know you're on the latest version too. I can't think of any other reason the 1124 and 1125 enum would report different temperature values for the same voltage ratio because like you said, they use the same equation in the libraries.
berkinet
Phidgeteer!
Posts: 95
Joined: Thu Sep 17, 2009 12:17 pm
Contact:

Re: Sensor value is ouside the valid range...

Post by berkinet »

mparadis wrote:The numbers you gave match up almost perfectly:

0.535 v/v -> 57.766 °C on the 1125's temperature sensor (or 1124)
0.535 v/v -> 61.771 %RH on the 1125's humidity sensor...
You were right. I must have not been paying close enough attention and had selected the humidity sensor. Sorry for wasting your time :oops: