Posted: Mon Aug 31, 2020 5:30 pm
by JuanC
In the Phidget control panel, the RTD input is giving error Saturation Detected.
I disconnected the RTD probe and still have this error.
What is going on?
Re: What to do about RTD Phidget (TMP 1200) giving saturation detected error
Posted: Tue Sep 01, 2020 7:44 am
by mparadis
The saturation error can also mean that there's no probe connected or there's a break in the wire of the probe (because electrically, a disconnected probe looks the same as a probe measuring a very high temperature).
If you still get a saturation error after hooking the RTD back up, it's possible there's a break in the wire or perhaps the cable of the RTD got too close to the heat and the cables inside melted and shorted.