Digital output switching on PhidgetInterfaceKit 0/16/16

Posted: Thu Nov 01, 2018 10:03 am
by pdb
Are the outputs isolated? Or do they share a common ground?

I want to send a 24v signal to a PLC using the outputs.
They are rated to handle 30v.

The inputs on the PLC share a common ground and sinks the current.
The examples I have found all use the common ground on the Phidget outputs.
The Phidget needs to be wired to provide current switch 24v +.

Re: Digital output switching on PhidgetInterfaceKit 0/16/16

Posted: Thu Nov 01, 2018 10:30 am
by fraser
Yes they share a common ground on the 1012, and REL1101. For switching isolated relays you'd want to look at the

1017
https://www.phidgets.com/?tier=3&catid= ... rodid=1045

or

REL2002
https://www.phidgets.com/?tier=3&catid= ... prodid=723